schindler 400A Loadweigher issue

Posted By: Soco1

schindler 400A Loadweigher issue - 05/13/13 05:33 PM

Does anyone know the process to disable the loadweigher unit for the 400A MRL. Can we do this from the SMLCD board on the controller?

Elevator keeps cancelling car calls after several are placed as if it is a type of anti nusiance dumping.
Posted By: kiwinightstalker

Re: schindler 400A Loadweigher issue - 05/15/13 10:31 AM

thats probably because its been set up that way...dont know the answer but im sure you cant diasable loadweighing!!!...there must be a parameter somewhere to increase the anti-nuisence value...or might just have to set up the loadweighers again.
Posted By: uppo72

Re: schindler 400A Loadweigher issue - 05/16/13 02:23 AM

Anti nuisence is generally set via specfic pre set weights. Check the settings but its more likely your loadweighing is out and should be retested and zeroed.
Posted By: Soco1

Re: schindler 400A Loadweigher issue - 05/16/13 03:02 PM

Does anyone have a testing procedure for this unit? I don't want to miss a step rezeroing the loadweigher.

I am about to load test as well, so any information would be valuable to me.
Posted By: uppo72

Re: schindler 400A Loadweigher issue - 05/17/13 08:09 AM

Sorry mate 'swindler' is 1 company i've never really had much dealings with.