Home
Gen 2 mrl shutdown
Posted By: Jluff
Gen 2 mrl shutdown - 09/05/17 01:58 PM
Hi guys. Got a gen 2 that's shut down.
Mcss shutdown codes are
2703
2811
2720
Mcss monitor status is
NRD SHD INA IDL
Ocss event log is
Cpu stack warn
Software reset
Proc exception
Mcss msg timeout
Mcss msg sio error
Ring 1 msg ck sum
Ring 1 msg sio error
Car was nav
Front dtc
Delay car prot
Spb com error
Rbi com fail
Spi bus error
Dbss log is
900 mcss timeout
913 mcss warning
000 power on
303 vac under
004 power down
304 vac imbalance.
I also saw traction loss on one of thf menu status screens.
Car will not run on inspection and the car is in the middle of shaft in between floors
What do u guys think ?
Posted By: Jluff
Re: Gen 2 mrl shutdown - 09/05/17 10:39 PM
Also the controller is on top inside of shaft .. how can I move the car up to get to controller ?
Posted By: INTENTEC-Luan
Re: Gen 2 mrl shutdown - 09/06/17 01:04 AM
I think the MCSS board was bad,or fuse burned out.You can release the brake by one key turn on and press a red button on the little board.
Posted By: elmcannic
Re: Gen 2 mrl shutdown - 09/06/17 02:07 AM
I think your glad no one was in it.
(Sorry...but it's true)
Posted By: TacoTim
Re: Gen 2 mrl shutdown - 09/06/17 09:03 AM
Firstly is ocss nav? And 2703_> drive shutdown?
Posted By: Jluff
Re: Gen 2 mrl shutdown - 09/06/17 01:25 PM
Ocss car monitor is
A-** NAV M*
All fuses check out good. Unless I'm missing one sum where
I have no lights on safe 2, safe or gds
My ring 1,ring 2 , ocss, rsl, mcss, dbss, dcss lights are r blinking fast
My LD1 light is steady and LD2 is blinking fast and LD3 is blinking slow
Main line power checks out good and PSS power supply is green lit 24v
My mcss shutdowns are 2703 drive fault and 2956 PAL unsafe to run
2111 gateway fault , 2113 REM not configured 2720 ACP low ac trout(2720 not listed in fault paperwork write up)
My dbss log is
913 mcss warning
900 mcss timeout
304 VAC imbal
303 VAC under
Posted By: Jluff
Re: Gen 2 mrl shutdown - 09/06/17 01:29 PM
Which board is the mcss board ?
Posted By: Jluff
Re: Gen 2 mrl shutdown - 09/06/17 02:35 PM
Also my ucm n c relays r picked.
Posted By: Jluff
Re: Gen 2 mrl shutdown - 09/07/17 12:49 PM
Is it normal to not have a ucm and cpu reset button on thf small board in thf door jam ?
Posted By: Jluff
Re: Gen 2 mrl shutdown - 09/07/17 12:56 PM
Correction on the ucm and c relays. They r not picked
Posted By: DripCan
Re: Gen 2 mrl shutdown - 09/07/17 03:50 PM
Try M 2231 then hit reset button
Posted By: Jluff
Re: Gen 2 mrl shutdown - 09/07/17 05:56 PM
Thanks drip. But I have done that power on reset many times and still shutdown.
Posted By: Indirtwetrust
Re: Gen 2 mrl shutdown - 09/08/17 01:41 AM
The controller is in the hoistway? WTF? What state are you in again? So what do you have to work with, just a Service Panel Board mounted in a jamb or something?
Thank god for the regulation state!
Posted By: Jluff
Re: Gen 2 mrl shutdown - 09/08/17 09:17 PM
That's correct dirt. U need to b on top of car with hall door closed to get to controller
Posted By: Indirtwetrust
Re: Gen 2 mrl shutdown - 09/08/17 10:09 PM
That is a damn shame. And I thought the MRL hydros with the controller in the jamb was a bad idea. (Those aren't legal here either). Is it at the top floor or bottom?
Posted By: Indirtwetrust
Re: Gen 2 mrl shutdown - 09/08/17 10:13 PM
And what is the advantage of that as opposed to turning the controller around 180 degrees and putting a closet right there? Besides the cost of a door.
I guess this way the customers don't have to look at our plumber's cracks while we work in the controller closet. If only there was a dedicated room to put the controller in...
Posted By: DripCan
Re: Gen 2 mrl shutdown - 09/09/17 03:56 PM
if you did a hard reset not just power off then might have to get the Otis guys with there construction run button to move car to access controller there is a known relay problem also check your gov switch on side of car might be it clipped door lock an tripped switch i know from personal experience of picking lock in flight an tripping gov on car
Posted By: Josh H
Re: Gen 2 mrl shutdown - 06/01/23 10:27 PM
What was your course of action and what did the problem end up being?
Posted By: EElevator
Re: Gen 2 mrl shutdown - 06/03/23 03:53 AM
At least your car wasn't at the top floor when that happened. So you didn't have to carry 3,000 pounds of weights up the steps to load the car so it would drift down when you released the brake to get to the controller. I agree with dirt, these should be absolutely illegal. Ridiculous design fueled by greed.
Anyhow, if in that situation you don't need Otis to come out with run buttons, under the service panel board there is terminal strips with all important terminals needed. Safety string, construction run terminals, even terminals to jump more batteries in parallel if the batteries in the controller to lift the brakes are dead.
Posted By: Elevator 1
Re: Gen 2 mrl shutdown - 06/04/23 12:24 PM
Good morning, has anyone worked on a conquest lift - have an error code (there are no floor values set ) ?