Posted By: Bigshow79
Dover hydro with Ibm relays. - 12/26/21 01:23 AM
Car runs but doors wont open.I have 300dc at Da1 and Da2.
Posted By: Johnny
Re: Dover hydro with Ibm relays. - 12/26/21 02:45 AM
Open Armature, bad brushes ????
Posted By: Johnny
Re: Dover hydro with Ibm relays. - 12/26/21 02:49 AM
300VDC relative to what?? each other (answer above) referenced to negative on rectifier?? referenced to Positive on rectifier?? Do you have a door operator print??
Posted By: Jluff
Re: Dover hydro with Ibm relays. - 12/26/21 12:29 PM
I had this once on a DMC. . It was bad capacitor under door controller But it was intermittent
Posted By: slider
Re: Dover hydro with Ibm relays. - 12/26/21 04:38 PM
If you are reading 300vdc between DA1 and DA2, then motor armature is open, probably the motor brushes
Posted By: Bigshow79
Re: Dover hydro with Ibm relays. - 12/26/21 11:59 PM
Yes. I have a faded door operator prints. If i open the door with operator de energized. When its energized it will close it. Bad re
Posted By: john jay
Re: Dover hydro with Ibm relays. - 12/27/21 01:17 PM
I would look at the capacitors that are paralleled around the contacts on the open and close relays. One of them is most likely shorted.