#27584 - 08/07/19 07:19 AM Gen2 I overload
Yus123 Offline
Yus123  Offline
Hi Everyone
GEn2 XIZI Otis 1000kg if have a problem INS Down move about 30cm then stop, with TCBC error 1TH 2TH Drive error DVR : rollback start DRV : I overload
change the DIR on contact 0--> 1 INS and Correction UP OK, after DIR set back 0 and add 2 filler weight in car top lift possible Normal run for 24 hours then stop again the same issue. we already changed new drive OVFWW, swapped the DBR , checked the mechanical brake,, and the result remains the same.
Appreciate if you can help this problem
#27585 - 08/07/19 09:50 AM Re: Gen2 I overload [Re: Yus123]
Alex75 Offline
Alex75  Offline
Sweden
Did you enter the correct values from the old drive? and preform a new learnrun and loadweigh calibration?
I would look at some specific parameters to start with:
LoadW Type (Type of loadweigh device)
SysInert (Inertia)
Balance (Balance of the system in %, Car/Counterweight)
ALWcomp Corr (Correction factor for internally calculated loadweighing compensation torque, ect Rollback/Rollforward)
What kind of software does your drive use? (ect GAA30785CAF or another software?)
/Alex
#27642 - 08/21/19 07:47 AM Re: Gen2 I overload [Re: Yus123]
Yus123 Offline
Yus123  Offline
Load weight calibration could not do because 4 pad sensors were damaged and got calibration missing sensor during calibration, then LoadW type I set 0 rather than 3 (others lifts Normal set to 0 also).
Learn Run and Encoder adjust have done and succeed.
Balance 47%
Software GAA30762 BAF1, I swapped from old drive about the software.
Last week we swapped whole drive to other lift and working well, then I got the same issue whenever put another drive to this site.
#27643 - 08/21/19 07:53 AM Re: Gen2 I overload [Re: Yus123]
Yus123 Offline
Yus123  Offline
please find the attached pictures
load sensor.jpg (24 downloads)
Rotary Oildraulic
Old Otis badge.
Brakes,Coil,Rotor
KONE MX10 repair tool kit