Are there any spare io's on a TAC 20. Have a bad io for fire service and was wondering if I can assign it to a spare io or if its a board replacement
Posted By: gs264
Re: TAC 20 - 04/14/15 04:13 PM
If you have IMS there is a way to change a I/O.
I have ims would you be able to give me some tips. Never re asigned an io on a TAC before
Posted By: Silly
Re: TAC 20 - 04/15/15 07:06 AM
Right click on I/O port and you will have an option for add/change. It's not too bad, the crappy part is finding where the spare lay because the ports do not directly line up with the CONs.last few pages of the prints should give you the spare locations. Active high and active lows.
Thanks guys much appreciated.