Posted By: DripCan

Dover Composite - 05/04/15 09:22 PM

Have 12stop duplex that I will get a call that car stuck at floor not responding get there an running checked door locks all floors an gate also dcl an dol all good .Left there today couple hours later called back said car at 1 doors closed not responding customer said hall button will call other car.So we're do I even start if running in morning an no fault timers or selector LEDs on
Posted By: john jay

Re: Dover Composite - 05/04/15 10:50 PM

20 years ago this was our everyday world. You have to play detective and eliminate problem areas from your thinking one by one. A lot of times when a Dover was stuck at a floor it would be from what we called a CS lockup. The CS relay should pulse in and out, but things like a door lock bouncing would cause it to pull in and stay energized. You may want to look at that circuit closely. Also if you have worn leveling rings on the selector it can create problems. A wire relay checker from SEES was also an invaluable tool for checking out Dover Relays. When you pull a relay out be sure to wiggle it from side to side and not up and down, this causes the base pins to get bent. Good Luck.
Posted By: john jay

Re: Dover Composite - 05/04/15 11:03 PM

One other thought, a lot of times replacing the selector leveling board would be a place to start.
Posted By: jkh

Re: Dover Composite - 05/04/15 11:24 PM

I once received a call for the elevator broke down at dusk. Of course they didn't want to pay for over time. The next morning we arrive and the elevator was running. At the end of the next day, (you guessed it) the elevator went down at dusk.
What we found was when the new outside lights went on at night, the voltage dropped enough to shut the elevator down.

Sometimes you have to look outside (no pun intended) of the elevator system.
Posted By: NewMech

Re: Dover Composite - 05/05/15 03:50 AM

Floor level CS lockup is from a stuck button contact. CS lockup during a run is from worn selector guides.
Posted By: kiwinightstalker

Re: Dover Composite - 05/05/15 12:10 PM

Must be some AWESOME lights to drop the voltage that much!!!
Posted By: E311

Re: Dover Composite - 05/05/15 12:32 PM

It is sad when you think about it, this was our everyday at one time, has that much time passed??? It seems to have! The CS lockup, worn selector guides and slider switches, may want to check the selector "traveling cable", and of course those pesky IBM relays with the plastic coil liners that like to get brittle and brake, then the peices fall off into the relay contacts...
Posted By: iggy

Re: Dover Composite - 05/05/15 01:43 PM

E311 was right. might have CS stuck in, or FT malfunction.
Posted By: christycollett

Re: Dover Composite - 05/05/15 07:26 PM

Hey you Guys your hurting my feelings by recommending a relay tester from SEEs. How bout WizBang Mark V designed and built by a fellow IUEC member?

I have the CS Lock-up band-aid if you want it

Work Safe,

Jim elevatorinfo@att.net
Posted By: DripCan

Re: Dover Composite - 05/05/15 08:48 PM

ok had FT faulted out borrowed tester an found only one contact in CS working replaced an no calls as of now. Christy I will be contacting you because I got a told about control of live electrical source.Cant use SEES tool with power off.
Posted By: danzeitz

Re: Dover Composite - 05/06/15 10:40 PM

Wizbang mark v is our relay tester of choice.
Posted By: dkwoodham

Re: Dover Composite - 07/28/15 06:20 AM

Anyone have an idea where I can find a Dover Composite parts manual or parts list.
Posted By: jkh

Re: Dover Composite - 07/28/15 11:07 AM

PM an email address to me...
Posted By: Rolly

Re: Dover Composite - 07/28/15 01:31 PM

Is the car at floor level when you find it? Had one of these once that slipped traction on a zoning stop because brush did not provide enough slow down distance and CS lock-up occurred between floors.
Posted By: TC7

Re: Dover Composite - 08/01/15 04:26 AM

I thing to try is rig MGT to not time out for trouble shooting purposes . Maybe MG set times out and doesn't restart. I believe the timer fires to time out MG set. Also 12A timer and auxiliaries on motor starting contactor if wye delta start. Sometimes all you have is process of elimination.
Posted By: Kup

Re: Dover Composite - 08/11/15 07:31 PM

Does if have the rectangular black impulse push buttons with the metal mounting clips. If so, one of the instant door close contact may be bad on one of the buttons. If you put the car on independent service and the doors close without placing a call that will let you know for sure. Then remove the 305 from 1C button. If the doors reopen it's that button. If not reconnect the 305 wire on 1C and go to the next one until you find the bad one.
Posted By: dkwoodham

Re: Dover Composite - 08/25/15 06:48 PM

replying to message regarding Dover Composite service and troubleshooting manuals.

Desperately trying to locate on for my guys.

Give me a shout if you have any leeds.
Posted By: J-R

Re: Dover Composite - 08/27/15 07:01 PM

PM me your email address ill send you a Dover Library
Posted By: jkh

Re: Dover Composite - 08/28/15 06:10 PM

DK,
As I stated in my last post, PM your email address...
Posted By: Fduncan

Re: Dover Composite - 07/14/22 12:21 AM

I know it’s an old post but does someone still have a Dover library that they are willing to share? Thanks in advance.
Posted By: boomer

Re: Dover Composite - 07/14/22 12:23 AM

Are you looking for some specific info?
Posted By: Montana

Re: Dover Composite - 07/14/22 01:04 AM

Email address?
Posted By: Fduncan

Re: Dover Composite - 07/14/22 12:56 PM

I recently picked up a building on my route and here goes. I’m working on a 12 stop Dover composite. It is a duplex, but whoever had them before me removed the top mounted selector and installed some kind of electronic one on elevator #1, that elevator is currently out of service and to my knowledge has been for some time. That isn’t the one I’m working on though, the one I’m working on has original selector on top and was operating fine until about 2 weeks ago when the down calls on floors 2, 3, and 4 stopped working. It would take an up call but no down call from those floors. All calls worked on other floors. Over the past 2-3 days this elevator has stopped working completely, then it started going to random floors when any call was given, then without changing anything would start going from top to bottom nonstop cycling doors at those landings. After cleaning the sleds and the top mounted selector and checking and cleaning all of the ibm relays carefully it started working properly for about 10 minutes then started going from top to bottom again no matter what call was given. Then all of sudden while I was going prints that are on jobsite but not clearly not for this particular job the elevator started taking up calls and going to designated floor just fine, on the down call it would go to the floor below the designated call, cycle doors then go up one floor to designated call. After about and hours or so of that it started stopping at every floor cycling doors no matter what call or which direction. After a 17 hour day I went home last night, came back this morning and it’s back to running top to bottom. I’m at a complete loss, and I’ve only got one other composite on my route at the moment so I’m not real familiar with these. Any and all advice is much appreciated. Work safe!
Posted By: Bobbybolognie

Re: Dover Composite - 08/13/22 05:31 PM

Not sure where to post this but here goes.
Customer owns the old NY Telephone building in Newark, NY 14513 (near I90, Western NY between Rochester & Syracuse). Looking for some experienced with the Dover Composite System to troubleshoot & repair it. We’re trying to get the prints from TKE Elevator but not sure we’re going to get them. Please share this with techs that could help. Thanks Bob. 803-640-7096
Posted By: danzeitz

Re: Dover Composite - 08/13/22 09:41 PM

Email address
Posted By: Bobbybolognie

Re: Dover Composite - 08/14/22 06:18 PM

rvseverson@hotmail.com
Posted By: Upndn40yrs

Re: Dover Composite - 08/19/22 03:30 PM

What info are you looking for?
Posted By: Bobbybolognie

Re: Dover Composite - 09/20/22 02:20 PM

I was looking for someone to work on this elevator. Since my last post we got a scanned copy the original schematics. The quality is poor. Now I'm trying to get the schematics reworked so we can read them.
Posted By: BB King

Re: Dover Composite - 10/19/22 12:23 AM

Old post I know… but I picked up 4 composites(2 sites) this month and have a partial print on one. Would anyone be willing to share their composite library please.
Thanks in advance!