Posted By: ridevertical

Gen 2 won't clear fire service - 01/15/16 06:02 PM

I'm working on a gen2 that won't clear fire service. All inputs from devices appear correct. Runs fine on ph2, just won't reset. Any ideas?
Posted By: Alex75

Re: Gen 2 won't clear fire service - 01/16/16 09:44 AM

GECB/TCB(C) Status menu shows what? (M-1-1-1)
Posted By: Magic smoke

Re: Gen 2 won't clear fire service - 01/16/16 03:02 PM

Won't reset from the keyswitch or from the service tool? Do you have a fire panel keyswitch or a remote fire service keyswitch? Check for that input?
Posted By: Alex75

Re: Gen 2 won't clear fire service - 01/16/16 04:56 PM

it might be the parameter EFO-EX, that is set to only allow Phase 2 of the Fireman opration to end at the EFO floor (Where the EFS keyswitch is located). If you get the sequence wrong, it can be real murder to get it running again.
Posted By: Vatorgator

Re: Gen 2 won't clear fire service - 01/17/16 12:55 AM

did you try the pf ram reset, worth a try
Posted By: Hotsauce

Re: Gen 2 won't clear fire service - 01/21/16 12:52 AM

Had the exact same issue a month or so ago. Don't still have the issue do you?
Posted By: ridevertical

Re: Gen 2 won't clear fire service - 01/26/16 10:21 PM

Still haven't cleared it yet. I don't believe my service tool is interfacing properly. It's a late model gen2 and my service tool is a couple years old. I tested my tool on another unit on my route and it works fine.Is there a way to do a hard reset w/o using the tool?
Posted By: Rolly

Re: Gen 2 won't clear fire service - 01/27/16 01:35 AM

What happens if you tell it that it has NO fire service? Then POR.
Posted By: NewMech

Re: Gen 2 won't clear fire service - 01/27/16 04:46 AM

Get the car at the recall landing with the doors open, turn the key in the hall station to reset and then off. PF ram reset is M-1-5-1.What type of Gen2 controller do you have? 311 with an MLB or GCS?
Posted By: CM1981

Re: Gen 2 won't clear fire service - 01/27/16 03:57 PM

I had a TXR5 that did the same thing at a plant. They had no key switches though and no smokes. It was the craziest thing is every seen. I even manually jumped the ports to make the I/Os come hi to low in the sequence the key switch would go and never got it cleared. Sold them a Smartrise Mod over that deal is how I fixed it.
Posted By: Magic smoke

Re: Gen 2 won't clear fire service - 01/29/16 04:54 AM

C1RS, C5RS
Posted By: Magic smoke

Re: Gen 2 won't clear fire service - 01/29/16 04:55 AM

Any new info?
Posted By: ridevertical

Re: Gen 2 won't clear fire service - 03/04/16 12:47 AM

Hey guys, sorry I didn't respond sooner. The tool I was using wasn't working right. I tried a different service tool and performed the pf RAM reset and I'm back in business. Thanks for all of the advice.