400A Schindler Elevator - 03/08/16 06:25 PM
We recently took over two Schindler 400A Elevators (not by choice!!) We are currently having an error 11 - FC_Block. Shut down error states the motor control goes to the blocked state...any suggestions as to where to look??? Or how to fix this error???
Posted By: sccjr
Re: 400A Schindler Elevator - 03/09/16 02:05 AM
Replace Drive. 400A's notorious drive killers. Also check motor encoder.
Posted By: EMS-WOR
Re: 400A Schindler Elevator - 03/09/16 02:21 PM
Thank you for the information.
Posted By: Ken1
Re: 400A Schindler Elevator - 04/05/16 07:08 PM
There is a relay inside the drive that goes bad, if you replace it take it apart and look, on size drive uses an ice cube relay and the other uses a contactor.