Posted By: bryanb
Kone kdl16 drive parameters? - 08/23/16 10:31 PM
I am looking for a list of Kone kdl16 drive parameters. Can anyone point me in the right direction?
Posted By: koneisland
Re: Kone kdl16 drive parameters? - 08/24/16 06:01 AM
Send me your e-mail address.
Posted By: NYTECH
Re: Kone kdl16 drive parameters? - 10/27/16 07:51 PM
I have a kdl16 and sporadically get fault 120 with sub code 1025.
I'm have the FAULT LIST for the previous drive V3F16L and for the 120 FAULT SUB CODE IS 2025.
Is it 1025 sub code the same as 2025 sub code ?
Posted By: NYTECH
Re: Kone kdl16 drive parameters? - 10/27/16 07:52 PM
Does any body have the FAULT LIST FOR THE KDL16 ?
Posted By: BRG
Re: Kone kdl16 drive parameters? - 10/28/16 09:01 PM
The 120 subcode 1025 says no motor current or one phase is missing.
Posted By: NYTECH
Re: Kone kdl16 drive parameters? - 11/20/16 03:41 PM
Thanks for responding. GOOD TO KNOW FOR EVERY ONE
This KONE stop every day with the 120, sub code 1025. It is always found perfect leveled at the floors. We have a straight shielded power cable between the DRIVE and the machine. Three black wires, one ground and the shield. We verified all connections, made sure the ground wire is connected to ground at both ends and the shield is ground at the controller end. WE REPLACED THE DRIVE ($7,000.00) from KONE SPARE.
STILL SAME PROBLEM.
The problem happened once in front of me. The DRIVE lift the brakes, I heard the high frequency noise like for a second, then stopped and faulted to 120-1025.
It looks like the DRIVE first energized the machine and verify there it is current flow through the three wires.
I'm thinking it could be the machine.
Does any one had this experience ?
Posted By: NYTECH
Re: Kone kdl16 drive parameters? - 11/20/16 04:06 PM
Elev8, if you still need the parameters, send me your email
Posted By: Indirtwetrust
Re: Kone kdl16 drive parameters? - 11/20/16 05:47 PM
Sounds like a contactor problem. Do you see any voltage drop across the contacts?
Posted By: NYTECH
Re: Kone kdl16 drive parameters? - 11/20/16 06:46 PM
The first thing I did with the original DRIVE was to take it apart and test those contractors, but now we have the same problem with the brand new DRIVE.
Posted By: BRG
Re: Kone kdl16 drive parameters? - 11/26/16 03:20 PM
The first thing I did with the original DRIVE was to take it apart and test those contractors, but now we have the same problem with the brand new DRIVE.
Is this the only error you're getting? I would clear the errors and get a list of all of them. F-1 is the most recent. If there are several, get the list in the order they occurred and get them posted. I adjusted several of these units before going into the service department.
Posted By: koneisland
Re: Kone kdl16 drive parameters? - 12/16/16 03:33 PM
Have had a few similar faults which turned out to be caused by faulty brake pods
Posted By: Hunter
Re: Kone kdl16 drive parameters? - 06/13/18 09:04 PM
We had the same faults. It ended up the brake would slip once the e-brake picked. Recalibrated brake pads pick gap to <.004.
Posted By: UpandDown2321
Re: Kone kdl16 drive parameters? - 06/14/18 04:11 PM
Old thread but this is usually solved by turning 6-12 to 0
No drive stand by mode...Some drives take years to show that problem others only a short time after installation
Posted By: Ottawa613
Re: Kone kdl16 drive parameters? - 06/27/18 10:54 AM
I'm experiencing some issues with a Kone kdl16 drive, constantly seeing a 120 fault with a sub fault 1025 - tried resetting the fault but it keeps re-appearing. Changed out the 201:1 and 201:3 contacts, checked all connections and still coming back. I have no information on most of these parameters. COuld someone please send me a complete listing of all the parameters / sub faults.
Thanks
Posted By: Ottawa613
Re: Kone kdl16 drive parameters? - 07/04/18 09:25 PM
We’re you ever forwarded the parameters? If so, could you send me them...need them to reference