LRV3 - replacing Memco EPD with new Door Detector.

Posted By: hirise

LRV3 - replacing Memco EPD with new Door Detector. - 09/30/16 07:33 PM

Can I place the new door screen dry contact across terminals EP1 and EP2 or eliminate the EPD wiring and place the contact across the LRCU (Light Ray Curtain Unit ?)terminals, B4-B5; input IM3-4, RVD2.

I also note a resistor in parallel across the light ray contact. Is this typically existing or an option that needs to be added to a light ray setup. (Haven't checked out the I/O board yet)

Thanks!
Posted By: LA Tech

Re: LRV3 - replacing Memco EPD with new Door Detector. - 10/01/16 10:39 PM

However you hook it up you just need to feed RVD2, just make sure you do not have a switch in front of the door detector contact as shown when using a LRCU that will disable your only reopening device. A parallel resistor across the contact is not necessary.
Posted By: hirise

Re: LRV3 - replacing Memco EPD with new Door Detector. - 10/03/16 01:41 PM

Thanks LA