smartrise traction fault A152 over/undershot - 03/07/17 01:52 AM
hi guys cant find this error in the manual it stops at A148 keep finding the car low in the basement with this error, reset and it will run for a week andcome back.
Posted By: InFritzWeTrust
Re: smartrise traction fault A152 over/undershot - 03/07/17 03:43 AM
My manual only goes to A148 also. Better call Smartrise in the morning. The debug menu should have some history and a description of all of the faults and alarms that it has logged.
If I were to take a guess I would check for worn selector tape guides. If the guides are worn the hole count could be off and overshoot a floor, perhaps.
Posted By: kenelev
Re: smartrise traction fault A152 over/undershot - 03/08/17 03:47 AM
infritzwetrust is right, check tape guides.
Also, do you have A60 error on fault log before A152?
If so go to adjust parameters 13-097 from x00 to x04
Re-learn the shaftway.
If car overshoot floors, depend of the contract speed check your slowdown settings is it correct.
Posted By: JimboNJ
Re: smartrise traction fault A152 over/undershot - 03/09/17 12:40 PM
Thanks guys. Will go to the guides next. Stay safe
Posted By: JimboNJ
Re: smartrise traction fault A152 over/undershot - 03/10/17 06:53 PM
Hey guys. They sent another mechanic to Job to replace guides at last shutdown. There was the F71 speed dev error with the A60 position error. Will see if the guides help Thanks again you guys are great. Love this forum
Posted By: green sleeves
Re: smartrise traction fault A152 over/undershot - 03/16/18 04:31 PM
Wht was the final resolution for this problem. I'm experiencing the same problem.
Posted By: JimboNJ
Re: smartrise traction fault A152 over/undershot - 03/25/18 10:05 PM
Guides and parameter adjustment