Home
Gen 2
Posted By: Jluff
Gen 2 - 03/16/17 01:42 PM
Got a gen 2 Mrl 4 stop. Keeps intermittently shutting down top floor on Saftey chain open.. have to hit the gov reset button to get back in service. Any ideas of why this may happen ?
Posted By: Rolly
Re: Gen 2 - 03/16/17 01:58 PM
You checked tail sheave in Pit? Really need a fault list.
Posted By: Jluff
Re: Gen 2 - 03/16/17 02:02 PM
Where should I go for fault list ?
Posted By: pieman
Re: Gen 2 - 03/16/17 02:03 PM
Gov reset or UCM reset ? Hitting gov reset shouldn't do anything unless your in safety test function I thought ?
Posted By: Jluff
Re: Gen 2 - 03/16/17 02:06 PM
It's the trip reset button
Posted By: john jay
Re: Gen 2 - 03/16/17 02:20 PM
have you checked the car speed, and Governor trip speed with a tach?
Posted By: Jluff
Re: Gen 2 - 03/16/17 03:04 PM
I will do that n gather more intell... no one is getting trapped in it. It's always level at the top landing.
Posted By: DripCan
Re: Gen 2 - 03/16/17 09:59 PM
check gov sheave depth with gauge an make sure tail sheave switch arm in center of two bolts
Have you put your eyes on the switch itself to make sure it is resetting fully every time?
Posted By: Jluff
Re: Gen 2 - 03/17/17 01:45 AM
It's been on the top floor each time. So I cannot look at switch until it's reset and running But it appears to be in proper position I will b back soon as it happens once a week.
Posted By: DripCan
Re: Gen 2 - 03/17/17 09:19 PM
sounds like your resetting UCM reset not gov reset if it was gov you would know where faults are you have to use tool for gov reset pushing button does nothing with out tool
Posted By: pieman
Re: Gen 2 - 03/17/17 11:39 PM
That's what I thought. Gov reset should only be operative if in safety function mode through the service tool . Sounds like you are either hitting CPU or UCM reset. Or are you going in through the tool to reset the governor ?
Posted By: Jluff
Re: Gen 2 - 03/18/17 12:38 PM
I have service tool. Just never had any training on it I have to learn everything on the job as I go. I can view the shut down messages which was Saftey chain and drive. I thought it was the gov reset I was pushing. It sounds like I'm wrong
I will try to get fault list next time. I was just asking for some guidance to navigate thru tool to them.
Posted By: Jluff
Re: Gen 2 - 03/18/17 12:42 PM
I was doin power on resets thru the tool and it wasn't resetting and checking the shut downs. That's all I did with the tool Then the shutdowns cleared after hitting what sounds like a reset on the controller in door jam on top floor That's what I thought was gov reset
Posted By: pieman
Re: Gen 2 - 03/18/17 01:39 PM
No worries jluff just trying to establish what is happening . Haven't worked on a true MRL Gen 2 in ten years ( that was the only type of Gen 2 in the u.k where you don't need. Controller space ) . All of mine here have the controller exterior . With that type of controller the gov trip / reset button is a silver button on the maintenance panel above the moveable circuit jumper on the right hand side side ( above controller inspection controls ) it only functions if you go in to safety test functions ( m-2-2-5-1 on service tool ) and scroll through until you come to Gov trip or gov reset . You enable one or the other and then the button should work ( or quite often not as the solenoids in the governor tend to pack up ) . The buttons on the board are UCM reset button and CpU reset button . I don't know the setup in the door jamb with the controller in the hoistway tho to be honest so it could be the Gov trip/reset you are hitting . The fault lists you should look at are the OCSS event list ( M-1-2 ) the MCSS event list (M-2-2-2 ) ( this is the most important one ) and the DBSS ( M-4 ) . With the drive there are two fault logs one gives you a history in a format that looks like this
F58 R20 F56 R45. Etc ....
The f number is a fault code and the R number is the amount of times it ran between the faults . To clear the ocss and mcss fault logs go into the log to view the faults and hit blue 5 blue enter . To clear the drive faults is an option at DBSS menu.
Next time you get the fault make a note of all the info in the above event lists and then clear them all . Let us know what they say . Hope this helps .
Posted By: Jluff
Re: Gen 2 - 03/18/17 01:50 PM
Thank you pieman. That helps a lot
Posted By: pieman
Re: Gen 2 - 03/18/17 02:07 PM
If it is the UCM reset you are hitting ( and after certain faults you have to ) and the elevator is faulting out at floor level I would have said a very likely culprit is the brake switches , as they are quite a common fault . However that would not explain why always the top floor ? When the fault happens do you find it bang on floor level at the top ? I'm wondering if you are getting 'roll back ' when trying to go down from the top ? Anyway ...take a look at the logs/ events and that should point us in the right direction .
Posted By: rami410
Re: Gen 2 - 03/20/17 10:29 AM
check level and slow speed magnets at top floor then you have to make learn run
Posted By: rami410
Re: Gen 2 - 03/20/17 11:24 AM
CAN YOU TELL WHICH CONTROLLER BOARD YOU USE
GECB I OR GECB II OR TCBC
if you have the service tool (AND THE CONTROLLER IS GECB II) , when you connect it you have
1 GECB 2 DRIVE
PRESS ONE TO ENTER THE GECB
THEN PRESS 1-2-1 READ THE EVENT LOG
IN ORDER TO ERASE THEM PRESS BLUE 2
THEN PRESS MODULE 2 TIMES
THEN PRESS 2 TO ENTER THE DRIVE
PRESS 2-1 READ THE FAULT
IN ORDER TO ERASE THEM AFTER U ENTER THE DRIVE MENU
PRESS 2-2 BLUE ENETR
IF YOU CAN GIVE ME THE EVENT LOG FROM GECB AND FAULT LOG FROM DRIVE I CAN HELP YOU
IF YOU LIKE ILL SEND YOU MY PHONE NUMBER AND YOU CAN CALL ME WHEN YOU ARE AT SITE
Posted By: rami410
Re: Gen 2 - 03/20/17 11:26 AM
if the problem is from brake switched it will give BS1-BS2 fault, and not all gen2 have brake switches.
Posted By: Jluff
Re: Gen 2 - 03/20/17 11:30 AM
Check your private message
Posted By: rami410
Re: Gen 2 - 03/20/17 11:42 AM
I have sent my no.
Posted By: pieman
Re: Gen 2 - 03/20/17 12:04 PM
All Gen 2 machines I have come across have brake switches . I would be surprised if there are any that didn't .
Posted By: rami410
Re: Gen 2 - 03/20/17 12:13 PM
it depends on the speed and load , all of gen2comfort which comes from Spain with 1m/s and loads up to 630kg comes without brake switches
Posted By: pieman
Re: Gen 2 - 03/20/17 12:48 PM
Ah ok , all of the ones I have worked on in the last ten years have been 350 f.p.m which all have brake switches and most have had faults on those brake switches at one point or another ! Do they use the Spanish machines much in the states ? I seem to remember when they used the Spanish machines in the U.K going back 15 years or so there was a lot of issues with the brakes ?
Posted By: Jluff
Re: Gen 2 - 03/23/17 01:55 PM
Ok guys here are the fault logs
Mcss
2000
2001
2002
2003 0001 330997
2201 0001 330998
2414 0027 002880
2610 0005 233173
2700 005 233175
2703
2704
Ocss
1000
1001
1002
1004
1101
1104
1201
1202
1500
1501
1502
1504
1505
Dbss
913
900
303
304
401
Manual reset is the button I hit to reset it
Posted By: pieman
Re: Gen 2 - 03/23/17 03:34 PM
Ok , without running through everything , the first bunch on the mcss are power failure / resets/ comms errors etc.. That you would expect to see after a power on reset. The ones of interest are
2700 ( not ready to run -brake dropped )
2703 ( drive fault )
2704 ( stop and shutdown message )
From here you need to look at the drive faults ,the one you're interested in is
401 ( brake SAS )
Basically means the brake switch(s) is in an unexpected condition , either your brake picked and the switches didn't or the brake dropped and the switches never changed state .
Either way sounds like brake switches . Quite a common fault on Gen 2 ( in my experience anyway ) the older machines Otis used to sell a brake switch replacement kit and it was a relative easy fix which worked well . On the newer machines I have only come across it once ( on an optimized 3.2 T machine ) I removed the rubber cover and cleaned out some dust and crap left over from construction and the fault went away .
The only thing throwing me is why always the top floor ? Unless maybe you are overshooting onto the limit forcing the brake do drop while the drive still ramped up and showing up as a drive fault ?
Posted By: pieman
Re: Gen 2 - 03/23/17 03:35 PM
Manual reset by the way I believe replaced the CPU and UCM resets from the older controllers.
Posted By: Jluff
Re: Gen 2 - 03/23/17 03:52 PM
Ok thanks pie. I cleared all the faults. I will inspect break switch and report back next time it shuts down.
Posted By: Jluff
Re: Gen 2 - 03/23/17 04:37 PM
I'm pretty sure the car is level at the top floor each time
Next time I will make sure of that.
Posted By: Rolly
Re: Gen 2 - 03/23/17 04:41 PM
How are you clearing faults? Hope your doing it with tool and clearing PF RAM.. M-1-5-1.
Posted By: Jluff
Re: Gen 2 - 03/23/17 06:39 PM
I cleared the ocss n mcss by goin into the logs n hitting blue 5 enter. The dbss was cleared thru an option in the dbss menu. I'm using the tool. I don't know if PF ram was cleared. I will see next time.
Posted By: DripCan
Re: Gen 2 - 03/24/17 01:13 AM
Ck your Bp relay an the little gray brake driver relays that mount on din rail marked xyz or something like that
Posted By: rami410
Re: Gen 2 - 03/26/17 09:32 AM
I totally agree with pieman the problem is with the fault
401
you have to check brake switches
can you tell which drive is installed?