Schindler 330a problems - 04/27/17 11:15 PM

This 330a is stuck in AST mode. I can run the elevator on inspection but it will return back to ast every time as soon as I switch it to automotic. When I reset the elevator controlls it also goes back into ast mode before it even tries to run. I checked the emergency terminal limits and everything is ok. The faults are a 107 pit oil switch, which this elevator does not have and a 1209, missing node. I checked the nodes on the smlcd and they all test out ok. Does anyone have any ideas why this elevator will not come out of ast mode?
Posted By: Indirtwetrust

Re: Schindler 330a problems - 04/27/17 11:44 PM

Did you do the double re-boot? If that doesn't work, you may need to drain the super-cap.
Posted By: Jluff

Re: Schindler 330a problems - 04/27/17 11:56 PM

I had similar problems and it was bad mother board
Posted By: 500fpm

Re: Schindler 330a problems - 04/28/17 12:14 AM

I did not do a double re-boot. How is this done and what does it do?
Posted By: Jluff

Re: Schindler 330a problems - 04/28/17 12:19 AM

Push button on the perpendicular board to the right of mother board ... push once then lights will flash then push again while lights are flashing.
Posted By: 500fpm

Re: Schindler 330a problems - 04/28/17 09:37 PM

The double re-boot worked! Thanks guys for your help.
Posted By: Philelevman

Re: Schindler 330a problems - 05/10/17 01:59 AM

Had a similar situation that would repeat once a week at first then every day after a while. Turned out the be a bad t cable wired in a shielded pair.