330A Inspection issue!

Posted By: mbke

330A Inspection issue! - 10/30/17 10:05 PM

33OA . Says on inspection . But all my inspection switches on car top, in car station and in machine room ring out ok and are in the run position. Changed CRIP board, changed CIOACD 3.Q. Checked I/O'S under status JREC (car top, Inactive = OK), (JRECC ,in car inspection inactive = ok) Drained GCIO 360 Capacitor 15 min, to .0070 vdc.

AND GO.......

THANKS
Posted By: jkh

Re: 330A Inspection issue! - 10/30/17 11:02 PM

I wonder if it would change if you disconnect the wires at the cpu?
Posted By: Indirtwetrust

Re: 330A Inspection issue! - 10/30/17 11:53 PM

Posted By: beaupeep

Re: 330A Inspection issue! - 10/31/17 02:00 AM

Replace GCIO
Posted By: elmcannic

Re: 330A Inspection issue! - 10/31/17 03:21 AM

On some equipment, car door/hall door bypass switch if turned on when the car is on auto will issue an INSP command. Confusing as heck if you're not ready for it.
Posted By: mbke

Re: 330A Inspection issue! - 10/31/17 06:23 PM

CHANGED ALL INSPECTION KEY SWITCHES AND CAR TOP INSPECTION ROCKER. STILL NOTHING.... ORDERED NEW SOFTWARE 3.61

WE WILL SEE...
Posted By: mbke

Re: 330A Inspection issue! - 11/01/17 05:15 PM

SOFTWARE CHANGE DID NOTHING. SAYING AT 3RD FLOOR.REALLY AT BASEMENT. ALL IN NORMAL POSITION. SAYS ON INS. 121X 6E FAULT. NEW SWITCH INSTALLED. STILL NOTHING...
Posted By: mbke

Re: 330A Inspection issue! - 11/01/17 05:18 PM

SAYS MISMATCH ON CAR TOP INSPECTION SWITCH . NEW SWITCH AND THE FAULT STILL IS THERE
Posted By: Peter iuec

Re: 330A Inspection issue! - 11/04/17 02:17 AM

Replace GC10
Posted By: ovideo04

Re: 330A Inspection issue! - 05/22/18 06:06 PM

Replace CIO board inside the COP with the same version.
Posted By: Tamperprufe

Re: 330A Inspection issue! - 05/22/18 10:15 PM

GCIO
Posted By: mbke

Re: 330A Inspection issue! - 12/21/18 12:42 PM

Thanks guys , I found a broken wire on the CIOACD . All better. !