dmc1 - 11/05/17 09:29 PM
I have a dmc that will not run up from 1st fl. you set car call the doors close and pump acts like it is bypassing, elevator goes no where and pump shuts down like its the low oil timer. it will run up and down on inspection. ran to 3rd/top floor. put in auto car leveled to 3rd. rode car to 2nd then to 1st. power was shut off, could I have lost programming
TSL contact or broken shunt, UTS contact, FST Relay contact
Posted By: Silly
Re: dmc1 - 11/06/17 01:17 AM
Doesn't the DMC run single coil in the up direction? Think it runs up fast only until slow coil is picked for slowdown, inspection is run on this up slow coil. My guess is bad UP fast solenoid or wiring to it.
Correct, FST picked, only picks up fast
Check your switches on the side of the car. Can almost guarantee you have a broken wire in your up slowdown TSL I think.
Posted By: elmcannic
Re: dmc1 - 11/07/17 05:37 AM
My vote for broken shunt TSL