Posted By: Philelevman
Tach 32 emergency power - 07/12/18 03:18 AM
I have a tach 32 stuck on emergency power. ENPN is low and I've tried injecting the I/O with no luck in correcting the problem. Had a bad storm over the weekend and they found it down on Monday. Ups is brand new and have 208 volts on all 3 phases. Tried swapping phases just in case but that didnt help either. Any suggestions?
Posted By: Huskervator
Re: Tach 32 emergency power - 07/12/18 11:53 AM
IOD Board is what I'd change. This time of year I carry a spare
Posted By: Indirtwetrust
Re: Tach 32 emergency power - 07/13/18 01:54 AM
I think it should be high but not sure off the top of my head. Try injecting it in the car and the group IO. I have seen a configuration that had a fuse on the din rail to feed the input. And I’m sure you have verified you have 120vac coming out of XFMR1, yes?
Posted By: Philelevman
Re: Tach 32 emergency power - 10/10/18 01:47 PM
Thanks for the help guys. Changed the IOD board and away she went