Kcm v3f25 intermittent 126 sub 2100 faults. - 08/04/18 06:14 PM

Car takes calls and leveling, load weighing, and terminal slowdowns look good. Happens about every 8 or 10 runs. Running at speed and no specific location in hoistway. Not terminals. Verified adon 3 hoistway and car safety chain inputs with meter set for minimum record.
Ideas?
Posted By: Rdwarrior

Re: Kcm v3f25 intermittent 126 sub 2100 faults. - 08/10/18 04:24 PM

adjusted 5-20-9 to 150 and good to go.
Posted By: Upndwn

Re: Kcm v3f25 intermittent 126 sub 2100 faults. - 08/21/18 10:39 PM

Did you change to an adon 3 board? Then changed 5-20-9 to 150
And problem went away?