Hello all. Looking for some information on the KONE KDM drive. I may have one that is bad but want to dig into it and see if there's and boards or components that can be troubleshot first. Any of you KONE guys have any literature you can share? Your help is greatly appreciated!
Posted By: UpandDown2321
Re: KONE KDM dirve help - 02/22/19 01:21 AM
What faults are coming up? Those have many subcodes and faults
I am only getting a 21 sub 2103 and a 26. I am blowing the F298-2 fuse and have a red and yellow lite on the drive I/O board blinking occasionally.
Posted By: Philly
Re: KONE KDM dirve help - 02/23/19 03:29 AM
21 is safe circuit. That is not the drive problem. What's subcode from the 26?
Posted By: OH boy
Re: KONE KDM dirve help - 02/24/19 03:21 PM
Not sure what fuse you are referring to (where is this located)
2103 machine room inspection
26 xt or xt1(thermistor)
The F298 fuse is on the KDA module. Come to find out it feeds the drive power supply and the buss inside the drive. There wasn't a sub code for the 26 fault. I have attached a page from the prints for reference.
Posted By: OH boy
Re: KONE KDM dirve help - 03/17/19 06:39 PM
Did you come up with a solution? Looks like the fuse comes off L2,L3 and should open contacts with K201 before going into the drive.
Posted By: OH boy
Re: KONE KDM dirve help - 03/17/19 07:44 PM
Also just found another set of prints, looks like 330 is your drive module fan!
Going to swap out the drive tomorrow. Stinkin Kone drives!
Success! New drive car is RTS.
Posted By: heisenberg
Re: KONE KDM dirve help - 03/22/19 01:08 AM
Always good to see a success story!
Posted By: Philly
Re: KONE KDM dirve help - 11/27/19 04:51 PM
Anyone know where the thermistor terminals are on kdm drive? I need print 1364622.