Posted By: Elevateyou
Schindler 330a er0094 block error - 05/01/19 12:11 AM
Schindler ER0094 block error keeps coming replaced the SDOOR AND CDOOR RELAYS changed all the door locks and gate switch still comes up any suggestions
Posted By: Updownman
Re: Schindler 330a er0094 block error - 05/01/19 02:58 AM
Keep the tracks very clean and the ramp lubed up well.
Posted By: Jblack83
Re: Schindler 330a er0094 block error - 05/02/19 03:38 AM
94 Error FATL. Only resets by turning lift off while on inspection. Once rebooted, turn off inspection. Should be gone. If it comes back you need to read the sub menu error code. In the fault log. That number will tell you which area to look at. There are Litterally 99 reasons why you are getting a 94 code.
Posted By: Elevateyou
Re: Schindler 330a er0094 block error - 05/12/19 04:39 PM
Fixed the 94 block issues now getting a 20- position lost fault - extra 0x00000067 do not see this fault in the manual has anyone experienced this if so can you help out?
Posted By: UpandDown2321
Re: Schindler 330a er0094 block error - 05/12/19 11:31 PM
If Im not mistaken that is re leveling failed. The car didnt move quick enough. Check the bypass setting if its taking too long to move and it goes to re level it will send out that fault.
Posted By: Wrench6
Re: Schindler 330a er0094 block error - 05/15/19 05:45 PM
Check R176. Bottom left of the main board. It's likely cooked.