Posted By: wltr00

Montgomery HH2 - 05/09/19 06:45 PM

I've got a 2-stop old Hydro unit that is floor level with the doors open. It will run up/down on INSP, but will not run up/down on auto.

Please see the attached prints.

Attached File
IMG_02141001.jpg  (51 downloads)
Attached File
IMG_02151001.jpg  (37 downloads)
Posted By: john jay

Re: Montgomery HH2 - 05/09/19 07:20 PM

Will the doors close on auto? what relays are energized? need a few clues.
Posted By: wltr00

Re: Montgomery HH2 - 05/09/19 10:47 PM

Doors will close on INSP but not in AUTO.
Posted By: elmcannic

Re: Montgomery HH2 - 05/10/19 03:23 AM

Did you get it figured out today?
———————————————————-
Status of DOP, DO and PC in controller?
Safe Edge contact?
Door Board test/manual switch set incorrectly?
Operator Relays?
Stuck DOB?
Just a few ideas....
Posted By: john jay

Re: Montgomery HH2 - 05/10/19 06:19 PM

The print is hard to read, but it looks like you have to pick UDX to drop the DO relay. The UDX relay is picked with a direction, either up or dn. The common link in the direction circuit is, from what I can make out either LR or IR relay. take a close look at those associated contacts and relays. You should come up with a solution. Good Luck.