TAC20-03 B44 Issue - 09/07/19 02:54 AM
Why is this TAC20-03 showing B44? I have checked with everything related to A17/B44 in the settings and it is still showing B44.
Please see attached picture.
Posted By: Indirtwetrust
Re: TAC20-03 B44 Issue - 09/07/19 03:47 PM
I would put the car on inspect, clear the faults, reset CPU, clear faults again then take it off inspect. If it still goes on B44 it should at least give you a specific fault to go on.
Posted By: Rolly
Re: TAC20-03 B44 Issue - 09/07/19 04:24 PM
I have to assume that when you change any of the settings like F16 you are doing a WRT after a change? Try changing F16 to no fire svc and see if the fault goes away if what indirtwetrust said doesn't work. He is really knows that stuff. He will get to bottom of the problem.
Posted By: elmcannic
Re: TAC20-03 B44 Issue - 09/08/19 04:18 AM
IIRC, the door inputs hall lock, gate switch then DCL had to be seen within a small window of time, and in that order. If not...B44.