Tac22 Car Call issue

Posted By: solidstate

Tac22 Car Call issue - 09/27/19 10:52 PM

Hall calls work as normal. Car calls answer the call, when car arrives at desired floor, door does not open automatically, have to press D.O.B. or the floor call again. Checked all magnets, parameters, inputs etc. Reloaded software also. Same thing.
Posted By: TC7

Re: Tac22 Car Call issue - 09/28/19 12:31 PM

Are you absolutely sure car is not overshooting and leveling back down?. I had this happen to me on Tac 32 hydro , didn't cause faults. I can't recall if it was only car calls that didn't open door, or car and hall.
Posted By: solidstate

Re: Tac22 Car Call issue - 09/28/19 01:33 PM

Yes we are sure of that have watched i/so and of course we are in machine room injecting calls and know that it is not overshooting
Posted By: elmcannic

Re: Tac22 Car Call issue - 09/29/19 01:04 AM

Sounds crazy familiar. Turn it onto Fire Service, then off, and see if that clears it.
Posted By: Al Carlson jr.

Re: Tac22 Car Call issue - 10/02/19 03:12 PM

Turn D32=2 , sounds like it 0 right now
Posted By: Tweeker

Re: Tac22 Car Call issue - 10/07/19 11:02 PM

What type of door operator are you using?
Posted By: solidstate

Re: Tac22 Car Call issue - 10/13/19 10:03 PM

We were able to get back to the job this week. Tried Phase one and Phase two, still same issue. D32 was on 0, we changed that to 2 and wrt with a reboot. Still same thing. Speed of this job is 125fpm, and speed is fine.
Posted By: Rolly

Re: Tac22 Car Call issue - 10/14/19 12:17 PM

Is there any faults in car with IMS? Also check group.
Posted By: Elevtech23

Re: Tac22 Car Call issue - 10/14/19 08:47 PM

make sure d26=0
Posted By: Rolly

Re: Tac22 Car Call issue - 10/15/19 01:50 AM

Might not be a bad idea to change D26=1 then change back to D26=0 since you loaded new software into board. Since you had D32 at 0 no telling what could be wrong. possibly a glitch when loading.
Posted By: solidstate

Re: Tac22 Car Call issue - 11/21/19 09:49 PM

this may be premature......will know for sure after Thanksgiving. It appears to be the expansion board. We are getting in the 24 volts, but at test points only 16 volts, with all the cons unplugged.

More to follow.
Posted By: solidstate

Re: Tac22 Car Call issue - 12/02/19 10:11 PM

We hooked up the new expansion board and the same thing. Thyssen thinks bad board, and are sending another one. We will bench test the next one before we hook up and then test afterwards. Keep it updated as we find out more.