Kone KCM831 Fire Recall

Posted By: Safetyguy

Kone KCM831 Fire Recall - 12/30/19 12:03 PM

Neither the phase 1 or phase 2 key switch have any effect on the operation of the elevator. These key switches were functioning properly a month ago. Seems the system has dropped recall.

I'm uncertain how to check the parameter settings. Also do not know which parameter would need to be checked. I do not have any special tools for Kone.

Please let me know if there is something I can check through the menu system that is part of the controller.
Posted By: lowoil

Re: Kone KCM831 Fire Recall - 12/30/19 12:48 PM

Menu 1 sub menu 62 should equal 1
Posted By: Safetyguy

Re: Kone KCM831 Fire Recall - 01/03/20 08:44 PM

Very helpful, that was what I needed. Thank you
Posted By: Safetyguy

Re: Kone KCM831 Fire Recall - 01/03/20 09:41 PM

Is there a particular procedure to reset the controller after testing the oil timer?
Posted By: lowoil

Re: Kone KCM831 Fire Recall - 01/04/20 08:43 AM

Pull xm16 off for a few seconds