Posted By: kenelev
DMCI hall call problem - 06/03/20 07:55 PM
Have a duplex DMCI, problem is hall call keep latching by itself and when either elevator go to those call it will not cancel the call either.
Anybody have problem like that before?
Thanks,
Ken
Posted By: Mr.E
Re: DMCI hall call problem - 06/03/20 08:10 PM
If you have recently lost your parameters, I would check to ensure that the car ID’s are correct. I’ve had similar issues on a duplex when the to units are fighting over which one is the master.
Posted By: kenelev
Re: DMCI hall call problem - 06/03/20 08:22 PM
car ID and master and slave parameter had been check already.
Can I switch master and slave from one car to the other?
Posted By: Mr.E
Re: DMCI hall call problem - 06/03/20 08:36 PM
You should be able to. Though if they are set correctly already, I wouldn’t worry about it. Have you tried turning one off at a time and seeing if the problem is Isolated to one car? Could be a bad CLC on one car, causing the issue for both.
Posted By: kenelev
Re: DMCI hall call problem - 06/03/20 08:44 PM
Will try it out tomorrow
Thank you,
Ken
Posted By: Adrian
Re: DMCI hall call problem - 08/08/20 04:32 AM
Log in and make sure your call cycling is turned off. Also check your
CLC - Adjustments- 30 to 34 confirm you have cars identified 1 and 2
Ihave 90 DMC 1 on my route and can help with whatever you need.