Posted By: EMEEL LLC

Dover Compumatic - 06/11/20 12:58 AM

Hi, with Dover computamatic controllers, I have problem with 4 elevators/15 story building. the dispatcher unit looks like disabled.
All elevators are running in wild operation (The elevators are running continuously between the floors and never stops , and the hall calls still stuck on and never cancel the calls.
We checked all the wiring between the dispatcher unit and the controllers; and even if we turn the dispatcher off the wild operations is still.
I could NOT figure out what is the problem and how we can re communicate these elevators with the dispatcher.
Thanks for helping,,,
Posted By: Johnny

Re: Dover Compumatic - 06/11/20 11:36 PM

What city are you in?
Posted By: Johnny

Re: Dover Compumatic - 06/11/20 11:37 PM

Check relay ATO, is it in? are all your wire contacts in ATO in good shape?
Posted By: Johnny

Re: Dover Compumatic - 06/11/20 11:48 PM

voltage from ATC to S+ ???
Posted By: Johnny

Re: Dover Compumatic - 06/11/20 11:49 PM

condition of NP Relay
Posted By: EMEEL LLC

Re: Dover Compumatic - 06/27/20 07:31 PM

thank you very much.
i got the problem solved.
some wire in dispatcher came off by loose connector.
Thank you very much