Home

TAC 32 Faults 1920 + 1920

Posted By: Elevator_Logic

TAC 32 Faults 1920 + 1920 - 08/26/20 11:48 PM

I have a TAC32 down with LCD reading 1920/1922 faults. This happened directly after storm power outage. The technican before replaced the IOD board and that did not fix the problem. I believe the Job Software needs to be reloaded. What is the procedure for doing that?
Posted By: Indirtwetrust

Re: TAC 32 Faults 1920 + 1920 - 08/27/20 12:09 AM

Check J16. It should be 18.
And you have to do an SPC after replacing the IOD. If J16 has changed to 0 and you did do an SPC after replacing the IOD, you will have to do another after changing J16 back to 18.
Posted By: Elevator_Logic

Re: TAC 32 Faults 1920 + 1920 - 08/27/20 09:44 AM

Okay I will confirm that

What is the procedure for reloading the job profile using the thumb drive in controller. I know it plugs into the main controller board and you then either hold a button down or select a option in the UIT.