Posted By: ubro96
Kone ecospace - 12/08/20 12:41 AM
Hey, crew, I'm getting a couple of faults 0188 and 0187 the car is doing a high-speed stop just after it leaves the floor. This morning when I got there the Overspeed switch was tripped
Any input would be appreciated
Posted By: heisenberg
Re: Kone ecospace - 12/08/20 03:45 AM
1) Ebrake failed to pick.
2) Ebrake/Rope gripper switch
failed. LED D182 failed to light
and/or D181 failed to turn off.
Terminal XEB2/7 remains at
20vdc. XEB2/5 remains at 0vdc.
3) Channel 2 has detected a fault
and does not allow the
Ebrake/Rope griper to pick
Press Yellow ACUM
Reset button on
ADON Board.
Posted By: Rolly
Re: Kone ecospace - 12/08/20 08:49 AM
You probably need to change the Brake Micro switches to low movement switches. One that works is Omron Z-15HD-B.