I have a 50-04 32 bit MRL that is showing rescue operation and cannot be cleared. The error log loops 1114 1907. Incoming power reads good as well as reverse phase. Figuring to start by changing IOC? My print doesn't show rescue circutry but the switch operates from IOC. Is that a direct swap?
Posted By: UpandDown2321

Re: Tac 50-04 Rescue - 07/20/21 11:22 AM

Changing IOC had no effect. Car still acts as if its in manual rescue mode
Posted By: Indirtwetrust

Re: Tac 50-04 Rescue - 07/21/21 08:11 PM

What is J16 set to? Should be 19
Posted By: UpandDown2321

Re: Tac 50-04 Rescue - 07/21/21 09:03 PM

I ended up finding that later on. Not sure why that would have changed but it cleared up after that. I thought IOC was no good when no inputs would update. Thanks for reply
Posted By: Indirtwetrust

Re: Tac 50-04 Rescue - 07/21/21 09:40 PM

It happens sometimes. Manifests differently depending on what it changed to.