Posted By: charly17267
Schindler 3300 - 07/29/21 02:28 AM
I have a Schindler 3300. The LU sensor was broken. after replace that the CPU give me error 4305 and i dont know how to make a reset to clear that error and I can't not use Cadi because the port Com 1 it's not 9 pins and only have 5 pines in line... any help would be appreciated
[img]http://[/img]
Posted By: Alex75
Re: Schindler 3300 - 07/29/21 01:23 PM
Go to menu 10 - Enter
Submenu 127 - Enter
Change the 0 to 1 and hit enter.
UCM fault should be cleared now!
/Alex
Posted By: charly17267
Re: Schindler 3300 - 07/29/21 02:35 PM
Thanks Alex75
I will do do that and i will let you know...
Thanks for your fast answers 🙏🙏👍👍👍
Posted By: heisenberg
Re: Schindler 3300 - 07/31/21 05:44 AM
com1 port is not used for cadi..
Posted By: charly17267
Re: Schindler 3300 - 08/02/21 03:34 PM
I did that but the 4305 fault it's not clear and the controller have the red error light on
Posted By: BRG
Re: Schindler 3300 - 08/03/21 12:51 AM
To reset the unintended movement the car has to be on hoistway access then go to menu 10 press enter go to 127 press enter make it a 1 and press enter. Some of the newer ones have a switch under the door bypass switches that can be slide in one direction to simulate hoistway access. Be sure to switch it back.
Posted By: BOJAN
Re: Schindler 3300 - 08/05/21 08:37 AM
Release elevator from blocked state by dedicated reset of
the tripped safety device.
To reset ucm fault
Hit enter
Number 10 will appear
Hit enter again, it will change to 101
Hit Up to change the 0 to 1
Hit enter
Reset SCPU
-:Car door safety contact opens at start
-:Verify the correct function of KTC, adjust KTC
accordingly.
Verify the correct installation of the doors and resolve any
issue found.
Posted By: charly17267
Re: Schindler 3300 - 08/12/21 06:08 PM
Thanks to the whole family for taking the time to help me.
The elevator it is working good 🙏🙏🙏👍👍👍