Posted By: Jluff

Otis 211 hydro - 08/17/22 01:13 PM

DCCB on screen. Very intermittent. Once every week or two. 2102 and 2651 (DCC input on IO board failed ) has anyone seen this b4? Where does the Dccb input come from .
Posted By: Indirtwetrust

Re: Otis 211 hydro - 08/17/22 05:00 PM

Do you have a print? DCC input comes from the N/C contact on the starting contactor. PMC for X-line, MC for Y/D.
Posted By: Jluff

Re: Otis 211 hydro - 08/17/22 08:17 PM

My starter contactor has no aux in play. Only L1L2L3 and the coil are wired up …. The only nc contact is inside the Siemens starter
Posted By: Indirtwetrust

Re: Otis 211 hydro - 08/17/22 11:18 PM

Maybe the softstart was added and something goofy was done. For a softstart the jumper from J66 to J67 should be on which ties DCC directly to the run output. Then you set Invert DCC to a 1. Maybe you could get that fault from a problem with the run output or the DCC input but I’ve seen a relay added to simulate DCC instead of jumping it to run and inverting it in software. If there are extra relays I’d look there. A 211 doesn’t need any extra relays for a Siemens softstart.
Posted By: Jluff

Re: Otis 211 hydro - 08/18/22 10:25 AM

I know the starter was just replaced this year before I got the job ….I will check that stuff thanks dirt. It’s strange that it’s extremely intermittent….
Posted By: Indirtwetrust

Re: Otis 211 hydro - 08/18/22 06:16 PM

The DCCB can also mean exactly what it says, that the delta driver on the IOBD board is failing. But I’d try to rule everything else out first.
Posted By: Jluff

Re: Otis 211 hydro - 08/18/22 07:16 PM

I think the IOBD board is obsolete from Otis.