I've got a 3-car group of GAL4 controllers and when putting on Fire Service 2 of the 3 cars recall correctly, but the third car recalls to the wrong floor for Primary or Secondary fire recall.
I'm thinking this is just a programming issue but cannot find where to program. Does anyone have documentation they can share on how to program a GAL4 controller especially for Fire Service? I have the GAL4 Manual but it doesn't provide much information on programming or Fire Service.
Thanks
Posted By: Goat

Re: GAL4 Fire Service - 10/28/22 08:00 PM

https://www.gal.com/wp-content/uploads/2020/02/GALaxy-IV-Manual-DSD-412.pdf

Page 7-34

Table 7-7: Emergency Services

Field Variable Min Max Initial Units Description

Fire Main Floor Bottom Floor Top Floor 1 floor Fire Main Floor