Posted By: Hunter
Garaventa 5200 Elvoron Low oil timer - 10/29/22 08:33 PM
After doing a pressure test on a Garaventa 5200 Elvoron it went into low oil fault. Does anyone have any information that would be helpful for resetting? Thanks in advance.
Posted By: solidstate
Re: Garaventa 5200 Elvoron Low oil timer - 10/30/22 01:39 PM
1. Turn on the inspection switch on the PLC
2. Check that the X12 input LED on the PLC is off
3. Press and hold the lowest floor call button (1C) on the COP for at least 3 seconds to clear the fault.
4. Return the lift to service.