Posted By: Upndown76

Miprom hydro - 08/30/23 03:05 AM

Replaced pumping unit. Now when I turn to automatic it immediately gets the low oil timer. I’ve adjusted the pot, replaced the card and card rack Any help in why this might be would be helpful
Posted By: EElevator

Re: Miprom hydro - 08/30/23 10:33 AM

Was the low timer a float switch on the old tank unit?

Code allows for a timer or switch for low oil protection
Posted By: john jay

Re: Miprom hydro - 08/30/23 04:12 PM

Sounds like PT input is high. That is the low oil input.
Posted By: danzeitz

Re: Miprom hydro - 09/08/23 12:49 AM

did you replace starter with pump unit? Maybe to a soft start?
Posted By: stanklerbin

Re: Miprom hydro - 09/08/23 06:58 PM

HA on relay board starts the time for low oil
Posted By: stanklerbin

Re: Miprom hydro - 09/26/23 01:45 AM

My mistake.
UA relay picks and starts run times.

Apologies.
Posted By: Stall Protection

Re: Miprom hydro - 10/05/23 09:44 PM

Bump for visibility.

I'm in the same situation.
Posted By: Stall Protection

Re: Miprom hydro - 10/08/23 10:25 PM

My problem ended up being the TUS input. Lost a jumper with the removal of the old power unit.