Kone tms600 display error

Posted By: misigun

Kone tms600 display error - 10/03/23 02:17 PM

Hi!
I recently changed the main board in the v3f20.i put all the parameters and iam trying to do the learn guide but after I press ender to start, the elevator starts for 4sec and it stops giving me the error stfail.also I have an error e9 in the display of the tms600.any help?
Posted By: Jadam

Re: Kone tms600 display error - 10/03/23 02:36 PM

sftail = Start fail
Its normal tachometer fail..
Check that the tachometer scaling jumper is in the correct position on the control board 385:A1
Posted By: misigun

Re: Kone tms600 display error - 10/03/23 03:02 PM

All jumpers are in the same position as the previous board. Also in inspection mode elevator works ok but in normal mode nothing.
Posted By: Jadam

Re: Kone tms600 display error - 10/03/23 03:16 PM

What was the error before changing the board?
How old is the Nvram...
Also check all the can connections

E9 NET NOT WORKING
- There is something wrong with CAN connections
+ Replace processor board
Posted By: misigun

Re: Kone tms600 display error - 10/03/23 03:35 PM

The first is the display of the TMS that gives me the error E9
The second is the board of the v3f20 that I replace.the reason was that after 1m elevator stopped even in normal or inspection mode.

Attached File
Attached File
Posted By: Jadam

Re: Kone tms600 display error - 10/03/23 04:10 PM

Ok but check the other things and maybe use Ivmon to see if the fault is in the drive unit
Posted By: misigun

Re: Kone tms600 display error - 10/03/23 05:06 PM

What do you mean with processor board.
Do you have any manual for TMS 600 display errors?


Drive works perfectly on inspection mode.
Is it possible to have a fault and work on inspection?
Posted By: misigun

Re: Kone tms600 display error - 10/03/23 06:13 PM

Is this the processor board? If I order a new one do I have to do any adjustments besides jumpers ? Should I use the old ic's?
Thanks in advance!