Working on a kdl16
We got fault 0108 .we check and found encoder wheel defective.
Replace the wheel know We getting fault 0102.
We had to remove the weights to carry the lift below the top rloor
Posted By: MX4
Re: Kone elevator - 02/13/24 11:13 AM
What is the sub code of 0102?
The subcode I am getting is 2002
Fault 0102
Subcode 2002
That is the only fault coming up
Posted By: MX4
Re: Kone elevator - 02/13/24 07:06 PM
Drive DC over current fault
Measured drive DC current too high.
Wrong elevator parameters
Mechanical problem hindering movement
Broken or disconnected LWD feedback.
Posted By: MX4
Re: Kone elevator - 02/13/24 07:07 PM
Check your load weigher 5-1
The load menú 5 1 is at 0%
Menú 6 1=50
Menú 6 2=.5
Menú 6 3=1ms
Menu6 4=400
Menú 6 6=400
Menú 6 7=2
Menú 6 10=50
Menú 6 11=1000
The liftcapacity is 630kg
Every time I change it and try to move the lift it goes back to 400
Once change 6. 4. to 630kg it goes back to 400 kg
Posted By: MX4
Re: Kone elevator - 02/15/24 04:37 PM
You need to unlock the parameters I believe, 6-95 needs to be 0
Ok thanks much
I will check
in meanwhile check the motor cable termination at both end.
Also, don't forget that you have to save Drive Parameter before reset.
change 6-99 to 1 for save.
Good day all
So I got peogrammed all drive parameters.
I checked motor connection on both ends.
I actually replace the drive but same fault 0102.
Subcode 2002.
I was thinking of the load weighing device base on the subcode.
Can it be bypass
It is the strain Guage type connected to the ropes
Posted By: john jay
Re: Kone elevator - 02/20/24 10:44 PM
Are you picking the Brake/Brakes?
Posted By: MX4
Re: Kone elevator - 02/21/24 03:03 AM
So it started with a 108 fault and now a 102, both faults share load weighing issues. What kind of load weigher is it? What’s the part number for it or do you have a picture of it? Have you check 5-1 on all floors? Check load weigher connections? Check load weigher board? 6-75-65 will also show you load weigher input value in mA
First question is the car moving in RDF mode? (up and down from control panel)
Because Wight issue s for Normal ride (rated speed in car call)
PM me if you need help.