Posted By: Jluff

ESCO ELEVATOR - 04/18/24 01:35 PM

Hi

I have a 2 stop ESCO elevator intermittent shutting down.
Wiring diagram # DC -89-10618

Does any one have a print and any common problems with this thing. All small relays most 110v and bunch of artisan time capsules . I always find it on the bottom floor. Door will open but calls don’t stay latched
Posted By: Jluff

Re: ESCO ELEVATOR - 04/18/24 01:59 PM

Also forgot to mention a main line reset fixes it and it will run all day. Seems to shut down every other day.
Posted By: Bowtiedrooster16

Re: ESCO ELEVATOR - 04/18/24 07:48 PM

Could it be the low oil timer?
Posted By: Jluff

Re: ESCO ELEVATOR - 04/18/24 08:21 PM

That’s a good idea. Does anyone have any documents that show me which timers are what.
Posted By: Bowtiedrooster16

Re: ESCO ELEVATOR - 04/18/24 10:06 PM

I looked at an esco print I have on my phone and it looks like they use MT as the low oil timer
Posted By: Jluff

Re: ESCO ELEVATOR - 04/19/24 09:54 AM

Nobody has a print they can share ??? No ESCO pros out there ? Lol
Posted By: Bowtiedrooster16

Re: ESCO ELEVATOR - 04/19/24 11:08 AM

What year is the controller? I may have something close
Posted By: Jluff

Re: ESCO ELEVATOR - 04/19/24 11:38 AM

Hi. Thank you

This is the wiring diagram number
# DC -89-10618

480v

I think late 1980s but not sure

This is my email
joeluff11@gmail.com
Posted By: EElevator

Re: ESCO ELEVATOR - 04/19/24 02:33 PM

I sent you a pm
Posted By: Tramguage1

Re: ESCO ELEVATOR - 04/25/24 07:06 PM

Did you figure this one out?
Posted By: Jluff

Re: ESCO ELEVATOR - 04/25/24 07:16 PM

Yes. It was the MLT timer There was 2 motor leads tied together where the connection was coming apart