Kone E3000 - 01/29/13 02:20 AM

Anyone familiar with this fault on e3000 escalator? Upper ESE Comm flt
Posted By: Vic

Re: Kone E3000 - 01/31/13 01:58 AM

Mind if I ask you where you're located?
Posted By: Jaymmorris

Re: Kone E3000 - 02/08/13 05:13 PM

Dallas, tx
Posted By: E311

Re: Kone E3000 - 02/09/13 01:08 AM

do you know Terry Morris by chance?
Posted By: Vic

Re: Kone E3000 - 02/11/13 10:44 PM

The ESE board stands for "Escalator Safety Extension" board, located in either the lower, or upper wiring junction boxes. It communicates with the main processor board in the main controller through serial link, and some discrete wiring.

The various safety switches at each end of the escalator come into their relative ESE boards, and there are LEDs on each input, that indicate if the switch is active or not.

Kone puts ferrules on the end of their field wires, that spread the spring clips in such a way that the wire falls out of the clip with the slightest vibration. All you have to do is jump up and down on the floor plate, and some of these units will just shut off. Then you check the ESE board, and find that one or two wires just backed right out of their sping clip terminals.
Posted By: Jaymmorris

Re: Kone E3000 - 02/17/13 11:33 PM

Thanks vic and no e311, i dont know terry morris