I was recently asked to assist another elevator company on a Tac 20 problem. In the process of adding a soft starter they had made a wiring mistake that cooked the 188E board. They bought a new board from Vertex. Of course the board came as a generic board with virtually nothing installed. So given that they didn't have IMS much less a LONSTALK adapter, they were screwed.
I was able to obtain the original generic files and rebuilt the LON tree. The unit in question was installed around 2000.
Anyhow, the problem I am having is the car will run high speed and accept car calls BUT ... I cannot get the damn thing off of door disconnect. D26 flag is set to 0. I have tried toggling this to no avail. I am wondering if the problem comes down to a version issue with the 188E board.
Obviously, there have been several code changes over a 13 yr period. I was able to get the original carEEprom.dat file off the old board so I am pretty sure everything matches up. All the parameters I looked at matched the job conditions and the original floor count is right on. Do any of you guys know what I am missing?