#11110 - 06/25/14 01:31 AM MphII question  
Joined: Jan 2014
Posts: 32
Kone D Offline
newbie
Kone D  Offline
newbie

Joined: Jan 2014
Posts: 32
Anyone know what dach and dacc stand for on a Schindler mph print . Fuse 3 feeds dach then the door control board. Dacc is on the ground side.
Keep blowing fuse 3 replaced the door control board unplugged everthing and still blew fuse but doesn't blow when not connected to board.

#11111 - 06/25/14 02:49 AM Re: MphII question [Re: Kone D]  
Joined: Aug 2011
Posts: 563
uppo72 Offline
addict
uppo72  Offline
addict

Joined: Aug 2011
Posts: 563
Not sure but I wonder if dach is the + and dacc is the -. As to the fuse blowing, it is a little weird but I wonder if you've got a dud new board(however unlikely). The fact that it doesn't blow a fuse with the board disconnected, is also weird. Is the loom going to the board from the controller to the top of car? If so I would try to run a 'test' loom(outside of ducts/existing wiring) to prove your not getting some induced voltages in it, or a short that is only apparent when connected to the pcb. Anyway some food for thought.

#11112 - 06/25/14 03:39 AM Re: MphII question [Re: uppo72]  
Joined: Jan 2014
Posts: 432
Vatorgator Offline
addict
Vatorgator  Offline
addict

Joined: Jan 2014
Posts: 432
Dach and dacc is just the 115vac power supply to the door operator, it comes through the door switch on the controller, then to the power input of the door operator, the only other path, is that it feeds the controller board that lights the KDPO led in the controller. I believe that some of the door operators require a MDL type fuse, which is a slow blow fuse. if the board is new, try a slow blow fuse, if that does not work, put the door board switch to test, so that it is not trying to operate the door when power first comes on, you could have a bad door motor.

#11117 - 06/25/14 07:00 AM Re: MphII question [Re: Vatorgator]  
Joined: Mar 2014
Posts: 212
Silly Offline
enthusiast
Silly  Offline
enthusiast

Joined: Mar 2014
Posts: 212
I thought someone else used that nomenclature as well. DACH/Door AC Hot and DACC/Door AC Common.

#11119 - 06/25/14 12:26 PM Re: MphII question [Re: Silly]  
Joined: Jan 2014
Posts: 32
Kone D Offline
newbie
Kone D  Offline
newbie

Joined: Jan 2014
Posts: 32
I'll try some things today get back to you guys

#11128 - 06/25/14 11:06 PM Re: MphII question [Re: Kone D]  
Joined: Jan 2014
Posts: 32
Kone D Offline
newbie
Kone D  Offline
newbie

Joined: Jan 2014
Posts: 32
looks like dach and dacc go through a resistor and some blocking diodes then a zenor I think it's all in the main relay board just wondering if I should try replacing it. fuse three opens when I plug in the door control board with nothing else hooked up.

#11129 - 06/25/14 11:19 PM Re: MphII question [Re: Kone D]  
Joined: May 2011
Posts: 487
E-man Offline
addict
E-man  Offline
addict

Joined: May 2011
Posts: 487
There are 2 plug connectors on the DCB (I'm assuming it's a DCB and not a TDC?). I'd plug each one in seperately and see if just one blows it and/or both. I would of done the same, change the board. Did you use a known good board? Did you check the door motor? A FCB is involved also..

#11130 - 06/25/14 11:48 PM Re: MphII question [Re: E-man]  
Joined: Aug 2011
Posts: 563
uppo72 Offline
addict
uppo72  Offline
addict

Joined: Aug 2011
Posts: 563
I would still want to know if the loom going to the door board is ok. Take the board to the motor room and wire it directly there to see if the fuse blows. make a separate loom don't use the fixed one. At least doing this you prove the wiring isn't getting some sort of induced voltage or short. Maybe then the supply board might be faulty with that supply bridge you just described.

#11132 - 06/26/14 03:04 AM Re: MphII question [Re: E-man]  
Joined: Jan 2014
Posts: 32
Kone D Offline
newbie
Kone D  Offline
newbie

Joined: Jan 2014
Posts: 32
I unwired door motor and unplugged everything to door control board and still blew so I'm going to change relay control board tomorrow and see.

#11135 - 06/26/14 09:14 PM Re: MphII question [Re: Kone D]  
Joined: May 2011
Posts: 487
E-man Offline
addict
E-man  Offline
addict

Joined: May 2011
Posts: 487
Sounds like your rectifier is shorted on the RMH.