Lookin for some input or paperwork for a erl Westinghouse 74 vintage. Elevator runs too fast. Trying to figure what makes the voltage stops increasing once it gets to speed

#17575 - 07/20/16 12:28 AM Re: 2bc erl Westinghouse [Re: Ceege]  
Joined: May 2011
Posts: 487
E-man Offline
addict
E-man  Offline
addict

Joined: May 2011
Posts: 487
Is the car running away? Have you adjusted HS on the regulator?

#17579 - 07/20/16 11:35 AM Re: 2bc erl Westinghouse [Re: E-man]  
Joined: Feb 2013
Posts: 761
john jay Offline
old hand
john jay  Offline
old hand

Joined: Feb 2013
Posts: 761
ohio
try checking the Zener Diode.

#17583 - 07/20/16 08:47 PM Re: 2bc erl Westinghouse [Re: john jay]  
Joined: Jan 2014
Posts: 141
Boa Offline
member
Boa  Offline
member

Joined: Jan 2014
Posts: 141
NC
Not sure if this helps. On the older versions of the ERL controllers low insulation resistances to ground on the main loop circuits could cause overspeeding in one direction and not being able to properly compound

#17585 - 07/20/16 11:49 PM Re: 2bc erl Westinghouse [Re: Boa]  
Joined: Jan 2014
Posts: 432
Vatorgator Offline
addict
Vatorgator  Offline
addict

Joined: Jan 2014
Posts: 432
check the 6 relays in the motor field circuit. low motor field voltage will cause car to overspeed

#17633 - 07/27/16 09:56 PM Re: 2bc erl Westinghouse [Re: Vatorgator]  
Joined: Mar 2013
Posts: 15
Ceege Offline
stranger
Ceege  Offline
stranger

Joined: Mar 2013
Posts: 15
Tried adjusting hs pot and nothing, I'm gettin over speed in both directions, but what's weird is it randomly worked absolutely perfect for like two hours and right before I was going to turn it loose it permanently crapped out. We've had this on contract for five years and it never ran that good, don't know if that throws any other signs up. Thanks guy

#17666 - 08/04/16 12:52 AM Re: 2bc erl Westinghouse [Re: Ceege]  
Joined: Jan 2014
Posts: 736
Rolly Offline
old hand
Rolly  Offline
old hand

Joined: Jan 2014
Posts: 736
If the HS pot does not change anything you could have a Motor Field problem or a bad SCR or circuit Board Controlling Generator Field. Have you checked Standing, running, & forcing voltages? If you have more then one car, check and compare the Ohms in Motor Fields. Have you checked with a Tachometer how fast it is really going? Make sure you have no grounds in Loop Circuit.

#17697 - 08/08/16 06:40 PM Re: 2bc erl Westinghouse [Re: Rolly]  
Joined: Dec 2012
Posts: 8
B69T69 Offline
stranger
B69T69  Offline
stranger

Joined: Dec 2012
Posts: 8
Dixie CSA
Sounds like it might be shored look circuit to me look for shorted brush rigging's be be 10 meg of higher to ground.

#17709 - 08/10/16 08:45 AM Re: 2bc erl Westinghouse [Re: Rolly]  
Joined: Aug 2011
Posts: 563
uppo72 Offline
addict
uppo72  Offline
addict

Joined: Aug 2011
Posts: 563
Originally Posted By: Rolly
If the HS pot does not change anything you could have a Motor Field problem or a bad SCR or circuit Board Controlling Generator Field. Have you checked Standing, running, & forcing voltages? If you have more then one car, check and compare the Ohms in Motor Fields. Have you checked with a Tachometer how fast it is really going? Make sure you have no grounds in Loop Circuit.


Hey Rolly, what do you mean by forcing voltages? Which area?

#17710 - 08/11/16 12:07 AM Re: 2bc erl Westinghouse [Re: uppo72]  
Joined: Dec 2015
Posts: 1,541
Indirtwetrust Offline
ElevatorPractitioner
Indirtwetrust  Offline
ElevatorPractitioner

Joined: Dec 2015
Posts: 1,541
Local 18
He's talking about the motor field voltage/current. Forcing is full field.

#17711 - 08/11/16 12:36 AM Re: 2bc erl Westinghouse [Re: Indirtwetrust]  
Joined: May 2011
Posts: 487
E-man Offline
addict
E-man  Offline
addict

Joined: May 2011
Posts: 487
Does the car run fine (speeds are the same in both directions) on hand?

#17714 - 08/11/16 07:25 AM Re: 2bc erl Westinghouse [Re: Indirtwetrust]  
Joined: Aug 2011
Posts: 563
uppo72 Offline
addict
uppo72  Offline
addict

Joined: Aug 2011
Posts: 563
Originally Posted By: Indirtwetrust
He's talking about the motor field voltage/current. Forcing is full field.


Ah ok I understand now. I only ask as I haven't come across anyone in our parts who call it this, but just call it the pattern circuit s curve and loop circuit build up.


Photo Gallery
PECCO PH5000 Overspeed Governor
Drive sheave
The best helper.
Rotary Oildraulic
Old Otis badge.
Brakes,Coil,Rotor
KONE MX10 repair tool kit
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.046s Queries: 15 (0.011s) Memory: 2.7405 MB (Peak: 2.9582 MB) Zlib disabled. Server Time: 2024-05-15 09:07:46 UTC