Who's Online Now
0 registered members (), 8 guests, and 3 spiders.
Key: Admin, Global Mod, Mod
May
S M T W T F S
1 2 3 4
5 6 7 8 9 10 11
12 13 14 15 16 17 18
19 20 21 22 23 24 25
26 27 28 29 30 31
Newest Members
vacheera, KM Elevator, Shawzee, ChurchGuy, Luis Mariano
8461 Registered Users
Forum Statistics
Forums13
Topics6,525
Posts36,927
Members8,461
Most Online117
Jan 16th, 2020
Previous Thread
Next Thread
Print Thread
#31112 - 05/11/21 05:32 PM TAC 32 Issues  
Joined: Feb 2014
Posts: 32
travator Offline
Vtravis
travator  Offline
Vtravis

Joined: Feb 2014
Posts: 32
Hello, want to apologize for the long post but I am trying to include all of the information.

Initially this building took a power hit and we found issues with the CWIL. The P24A pico was blown and saw an obvious burn mark on the U13 chip. We replaced the CWIL.

Upon replacement, it was still showing offline with a DCN. We troubleshot the CAN back to the IOD and found only 15 ohms between CCL and CCH with con3 unplugged. I also had faults of 1920 and 1922. So both the IOD and CPUA were replaced.

With those replaced and software loaded on the CPUA, I now have 120 ohms on my CAN terminals. Unfortunately the problem remains. DCN shows maincop1 offline. On the CWIL, stat b is blinking erratically. On the IOD, both NPBAD and SPBAD LED’s are on. Tried an SPC and it says SP offline. Still have 1920 and 1922 faults.

Thanks in advance for any info!

#31113 - 05/11/21 07:41 PM Re: TAC 32 Issues [Re: travator]  
Joined: Oct 2015
Posts: 16
ernieschnerd Offline
stranger
ernieschnerd  Offline
stranger

Joined: Oct 2015
Posts: 16
Have you tried the TECC command to have the system configure the new CWIL? You may have to enter the TECCR command first to have any corrupted configuration of the CN reset.

#31115 - 05/11/21 10:34 PM Re: TAC 32 Issues [Re: travator]  
Joined: Feb 2014
Posts: 32
travator Offline
Vtravis
travator  Offline
Vtravis

Joined: Feb 2014
Posts: 32
I have done the TECCR, TECC a lot. I usually do three TECCR before the TECC. It actually says something like complete after TECC.

#31116 - 05/11/21 10:39 PM Re: TAC 32 Issues [Re: travator]  
Joined: Dec 2015
Posts: 1,541
Indirtwetrust Offline
ElevatorPractitioner
Indirtwetrust  Offline
ElevatorPractitioner

Joined: Dec 2015
Posts: 1,541
Local 18
Is there a CE electronics PI driver board? Unplug it, it fails often. If not, read DC volts from CAN high to ground and CAN low to ground. You should have about 2.5 vdc to high, slightly less to low, & they should both be fluctuating. If you see anything besides that, separate all the CAN nodes on the channel to see where the problem is coming from. The door board and the selector are nodes on the channel too. If it’s a Mod with the HDLM or Smartech II door operator that have the expansion board with UIT plugged in, that’s a CAN node too and I’ve seen it take the CAN channel down. The door will work fine with that disconnected. I’ve seen a power power spike kill every single device on the CAN channel 2.

#31117 - 05/11/21 10:47 PM Re: TAC 32 Issues [Re: Indirtwetrust]  
Joined: Feb 2014
Posts: 32
travator Offline
Vtravis
travator  Offline
Vtravis

Joined: Feb 2014
Posts: 32
Unsure on the CE board, will check tomorrow. Thanks for the info!

#31118 - 05/12/21 12:51 AM Re: TAC 32 Issues [Re: travator]  
Joined: May 2015
Posts: 71
TC7 Offline
journeyman
TC7  Offline
journeyman

Joined: May 2015
Posts: 71
Don't worry about SP and NP, those will start functioning when you get CWIL online. May have to reconfigure again since you tried that once when CWIL was offline.

BTW your goal for Can resistance is 60 ohms. That is set at factory by one 120 terminating resistor on CPUA, and parallel resistor on CWIL. Those resistors are part of the board and connected by board jumper. All other can resistors should be removed for car side(usually done in the field) most typically door board on hydro.

In my experience, the most common board to loose during power hit is CWIL. Sometimes IOD, and sometimes S24-3, but almost always CWIL.

#31121 - 05/12/21 12:00 PM Re: TAC 32 Issues [Re: travator]  
Joined: Feb 2014
Posts: 32
travator Offline
Vtravis
travator  Offline
Vtravis

Joined: Feb 2014
Posts: 32
No CE board. Diving in a little more this morning it seems we have lost the selector as well. I can establish communication to the COP with just the selector unplugged.

With communication to the COP I was able to successfully configure the SP and NP, but the bad LED’s remain on for both. Should I be able to get the SP and NP LED’s to good with the selector unplugged? Would be nice to be able to move the car on inspect to access the car top.

#31123 - 05/12/21 07:48 PM Re: TAC 32 Issues [Re: travator]  
Joined: Dec 2015
Posts: 1,541
Indirtwetrust Offline
ElevatorPractitioner
Indirtwetrust  Offline
ElevatorPractitioner

Joined: Dec 2015
Posts: 1,541
Local 18
No, you need the selector


Photo Gallery
PECCO PH5000 Overspeed Governor
Drive sheave
The best helper.
Rotary Oildraulic
Old Otis badge.
Brakes,Coil,Rotor
KONE MX10 repair tool kit
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.025s Queries: 15 (0.005s) Memory: 2.7068 MB (Peak: 2.8906 MB) Zlib disabled. Server Time: 2024-05-12 13:53:57 UTC