#2921 - 03/08/12 06:36 AM
Re: Westinghouse 3C2BC-ERL
[Re: kenelev]
|
Joined: May 2011
Posts: 487
E-man
addict
|
addict
Joined: May 2011
Posts: 487
|
Make sure these relays are up: 9 11A 90'S 60's (all) 29's 55 72T CC I'm assuming you checked all the fuses? Sounds like you have a 2CBC with a Frt?
Last edited by E-man; 03/08/12 06:37 AM.
|
|
|
#2954 - 03/13/12 01:28 PM
Re: Westinghouse 3C2BC-ERL
[Re: jkh]
|
Joined: Jan 2012
Posts: 885
jkh
4 Ever Learning.
|
4 Ever Learning.
Joined: Jan 2012
Posts: 885
|
Just wanted to close this out. The elevator has been running for 6 days now. We had to hand over hand the wiring to trace out the overlay for firemans service. There was nothing at the site and nothing on the prints. Adams (Schindler) claims they only have the prints for the original installation and nothing for the firemans service.
Vatorman15' Thanks for the info it was very helpful. Funny thing is that there wasn't switches in the shaft for 69x or 69x1. 69x & 69x1 are wired to the selector.
Again thank you for contributing.
Last edited by jkh; 03/13/12 01:33 PM. Reason: Spelling
Make good choices,
JKH
|
|
|
|
|
|
|