The easy things to check, if you have some spares are, to replace the NTS relay on the interface bd. Replace the Relay Pilot bd. Replace the MSU bd. Also, unplug and re-plug the feed wires. The NTS bd. feeds the NTSI input on the relay pilot bd. if NTSI goes low mid-hoistway you can generate a 39 fault. The relay pilot feeds the MSU bd. Also, the MSU generates the VC command, which is 8VDC. If the VC goes higher than the shadow volts of MI+/- 8.4 VDC the CO relay will drop out. Anyway, just some things to check. Good luck.