I had a smartrise do this once. Set your contract speed higher, a good bit above actual running speed. Couldn't get it to go away any other way. Would intermittently shut down for overspeed fault until I raised contract speed up a good bit. I'd watch it run and watch the speed fluctuate on the screen and set it 15-20 fpm higher than the highest you see.
Only problem may be you might not be able to have inspection run fast speed which would be miserable. I reckon you could try setting inspection speed to 140 and see if it'll still pick the fast speed with the valve. I usually always make inspection match contract on a hydro so I don't know what the controller would think if you made it a speed that wasn't one of its 2 speeds.