I got a 3 stop front and rear opening Schindler 2007 hydro .. I think Its a 330a or EIB.
After a double reset it will accept a call and take off. It will land and the doors will open and close but it will be shut down on a 0121 extra info all 0 until 7B at the end. I don’t see 7B extra info on my fault list. But i do see 78. Any help on this would be great. Also if I stop the car mid flight with controller inspection it will also throw the 0121 fault after I turn it back on normal operation
Note .. top of car switches look good. All lights go on and off as I wave my hand through the horseshoes . KLU AND KLD both are lit back on controller as it stops at the floor
Thanks no time. I see the leveling zone relay clicking on the crip board. But maybe it needs to be replaced. It’s not removable. So I guess I will bring in the whole board to repair shop
121 78 is level zone relay in wrong state after car stops. So your original thoughts are correct. Get a new relay on the board. I'd recommend changing the CD1,CD2 SD1 and SD2 as well while they have it