#37352 - 04/27/24 07:30 PM RCD redundancy fault. MCE  
Joined: May 2022
Posts: 36
Alto101 Offline
newbie
Alto101  Offline
newbie

Joined: May 2022
Posts: 36
Central Florida
HMC 1000 newer version. Troubleshooting this fault has been tricky. RCD redundancy fault. This elevator was shut down for 2 years. This elevator just needed some TLC and an inspection. Nothing was done to the controller or hydro system. Ran great for a month and this fault started.

CD relay has been swapped. Operates as it should. When a call is registered up or down the car will travel slightly then fault, back to normal then fault, intermittently. If the car doesn't make to the landing motor timer faults. Inspection seems to override this this issue. ( maybe it did RCD fault during inspection but definitely not like Normal, I don't recall this comment 100%)
one observation: When I first arrived next day after shutting down the car it took several call with no issue. Almost like things got warmed up and the fault started happening and got worse. Door close LED stays on during travel. Safety Circuit LED goes off during travel when RCD fault occurs. CD relay stays picked during travel and goes off when the car door opens as it should.


The better the effort, the better the result.

#37353 - 04/27/24 08:44 PM Re: RCD redundancy fault. MCE [Re: Alto101]  
Joined: Apr 2020
Posts: 402
Montana Offline
addict
Montana  Offline
addict

Joined: Apr 2020
Posts: 402
MCE Tech support 916-463-9200. Had about a 15 to 20 minute call back time last Thursday.

#37354 - 04/27/24 10:04 PM Re: RCD redundancy fault. MCE [Re: Alto101]  
Joined: May 2022
Posts: 36
Alto101 Offline
newbie
Alto101  Offline
newbie

Joined: May 2022
Posts: 36
Central Florida
It was certainly tech supported but all signals seem correct. Relay swap was first suggestion. Craig is usually very helpful but we had no success.


The better the effort, the better the result.

#37364 - 04/29/24 11:28 AM Re: RCD redundancy fault. MCE [Re: Alto101]  
Joined: Aug 2017
Posts: 448
EElevator Offline
addict
EElevator  Offline
addict

Joined: Aug 2017
Posts: 448
Do you have te book? This is the asme 2000 version since it has redundancy, but is it the normal f1-f8version or the newest version with more dips?

I'd swap ribbon cables next. I've had some odd issues in the past from ribbon cables that never move but connection got iffy (especially ecospaces). After swapping ribbon cables I'd run it to see if problem went away or you've ruled that out then move on to checking power at points on board and watching cpu inputs. See if there's any triacs on that circuit on the i/o board too.

#37381 - 05/01/24 10:27 PM Re: RCD redundancy fault. MCE [Re: Alto101]  
Joined: May 2022
Posts: 36
Alto101 Offline
newbie
Alto101  Offline
newbie

Joined: May 2022
Posts: 36
Central Florida
F1-8 switches. I have read the fault description troubleshooting. The next step is mentioned to replace the ribbon cable. RB20. Certainly give this a try but it seems doubtful to me.

Today I noticed a very distinct pattern. The unit would take calls to all landings, when the door reach fully open the controller would RCD fault. When the door reached fully closed the controller would "cycle test" and take the next call with no faults. same RCD fault at all floors when the door reaches fully open. The lock circuit drops and picks up as it should. CD relay energizes as it should. DCL and DOL signal correctly.

The room is excessively humid and hot with summer approaching (no ventilation). I noticed vapor droplets built up inside the relays. Oddly opening the door and working out some heat and humidity the fault stopped happening for multiple calls (not sure if this was a coincidence or effective, TBD)


The better the effort, the better the result.


Photo Gallery
PECCO PH5000 Overspeed Governor
Drive sheave
The best helper.
Rotary Oildraulic
Old Otis badge.
Brakes,Coil,Rotor
KONE MX10 repair tool kit
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.030s Queries: 15 (0.006s) Memory: 2.6855 MB (Peak: 2.8444 MB) Zlib disabled. Server Time: 2024-05-17 19:53:24 UTC