I am in the process of replacing a drive for an Ecospace. Unfortunately the dead drive parameters were unretrievable.
I installed the new one but didn't get to spend alot of time on it yet. It did not run on insp right out of the box. No drive demand or main contactor light. No error codes Either. Parameter 6-95? i think It's the communication parameter is right,
Unfortunatley I don't know the exact events leading up to the drive blowout but Kone and TK walked away from the job because it blew out a drive for each company when they were setting up loadweighing.
I found the problem, The load weighing current feedback wire XLW1 I think. IF you need the exact wire I can post tommorow, I'm old, I forget, sorry. was not in the Connector right, Pinched insulation, caused the drive to burn out when weight was put on to set the loadweighing, Found alot of factory problems lately with the eco's.
.
If anyone has replaced one of these 16 drives before I would really appreciate any help that is offered. I have the drive parameter sheets and the latest final commisioning book, but I don't have the drive replacement procedure write up. Thanks in advance for any help.