Hi
Having done loads of these mrls, the code 06 correctly mentions releveling problem, possible causes are, the oil thickening up, assuming you haven't got the oil heater fitted and struggles to flow through the valve, adjustment needed of the block.
ZP inductor faulty or the ZP magnet set incorrectly, make sure the inductor is no more than 15mm away from the magnet. I have also found the LP1 telemac relays to be unreliable at times, especially the add on blocks. The CRS module can also become faulty because the +/- module supply voltage percentage is not good. The power supply Connection come from igv set at 50 v ac input, this creates a 27 vdc output instead of the 24 v required, then the CRS modules become faulty creating 06 codes and failure to level and open the doors, move the input wire to 60v terminal on the psu board.
Rfs [up slow and stop] could cause a problem, but you would see it all the time during normal running, if it is fitted with rfs and rfd relays, try cleaning the contacts.
Best of luck
|
|
|
|
|