Wondering if anyone has run into the same problem...
I've got a couple of 3200 units that seem to stall after the M contactor picks.
High voltage board outputs MA and MB, but no P. Relay board U1 or D1, UD, SM all picked. DEN out...
Only drive signal showing on the relay board is the Drive Ready LED...
Car is always level with the floor, brake not picked, drive not energized, showing RDC low on RMS board... only odd thing is a flickering OK signal on map unit (output group 18?)...
Any thoughts? Happens every 2 - 3 weeks. Tipping a hall lock or cycling inspection will cause M to drop and car will take off...
flickering i/o you say. pull out the hvs 9603 board and measure all of the 4.7 micro farad capacitors. i think there is about 16 of them. replace all the bad ones.
One of the main issues Ive had with these is in the redundancy circuit (RE) If the contacts are not in really good shape you will get problems. If my memory serves me right its a 24vdc circuit. Also the drive contactor's aux. contacts are a known issue.
All contacts on the M contactor are fine... if I remember correctly, even if the NO contacts intermittently don't make, the controller would drop M... in this situation M is held electrically...
Luis.... you should start your own thread... your issue is a little unrelated to this one...