I have a bad tac 20 door operator board. I have replaced 2 other just like it and they worked fine. This one did not work.
Vertical Express said it was set up as a harmonic instead of a Linear and sent me a hyper terminal adapter and a couple manuals they told me I can change it, but I don't see where to do that. None of the parameters in the manual have a Linear vs Harmonic profile that I can see.
I have a laptop set up with the adapter as recommended by Vertical Express.
Any help would be appreciated.
I have the LD-03 Door Operator manual from Vertical Express & the Door Card Replacement Procedure for Card Series 6300PA_ & 6300ABN_
LDO is the parameter for linear door operator, 1=Linear, 0=harmonic. Did they give you the preset files to load through Hyperterminal? Can you talk to the doo with IMS or are you using a UIT?
They gave me the preset files for all door types, but they are corrupted when I download them for the email. They also gave me all the parameter info so I could enter the info manually.
Vertical express gave me info to set up a laptop with the hyper terminal which they tell me should work. I don't have a UIT. Although someone recently told me that a UIT for door operators only could be carried from job to job. If thats true, the boss may let me buy one.
I will try that parameter and let you know if it worked. Thanks for the help.